How to control a Brusa NLG5 charger with a WatchMon
Photo of Fan-Cooled Brusa NLG5 charger
Photo of Liquid-Cooled Brusa NLG5 charger
Adopting the Brusa NLG5 charger can be configured as follows within the WatchMon supervisor. It may be necessary to run a BridgeConnect with the twin canbus ports running in pass-through mode to provide ground isolation from the traction battery supply and WatchMon ground reference.
CAUTION:  Example below has values shown for a demo LiFePO4 cell pack, ensure you adopt values suitable to your application.
Step 1 - Install communication cable to charger via CAN port on WatchMon.
Step 2 - Install communication cable to Brusa NLG5 charger wiring socket.
NB: Add 120ohm terminating resistor to charging plug.
Step 4 - Select Canbus protocol to "Brusa NLG5 Charger" and Save.
  • Low power must be enabled.
  • When the bypass current for all CellMons is above Final the system will complete charging cycle.
Note: Make sure to "Device Sync" to update the changes to the CellMons.
In this example below the voltage was set to 310.8 volts, current to 4 amps and limited to 0.5 amps during balancing
  • Scaling must be 10 for both voltage, current and power.
Step 11 - Navigate to Telemetry, then Live Stats to observe system operation.
  • Live States telemetry