How to control a SMA Sunny Island inverter/charger with a WatchMon
Here are the steps to configure the SMA Sunny Island inverter/charger to the WatchMon supervisor.
CAUTION:  Example shown is for a demo LiFePO4 cell pack 16S1P, ensure that you adopt values suitable to your application and comply with the battery suppliers recommendation.
Step 1 - Install communication cable to charger via CAN port on WatchMon.
Step 2 - Install communication cable to SMA inverter wiring socket.
Sunny Island RJ45 pin 4 connects to Can-H WatchMon
Sunny Island RJ45 pin 5 connects to Can-L WatchMon
Only the Sunny Island CAN communication interface is connected to the BMS, the second communication line – SYNC Bus is not connected to the BMS.
Extract from Sunny Island configuration of RJ-45 plug "ComSyncIn" of :
Pin Signal
1 Sync1 – reserved
2 CAN_GND
3 SYNC_H
4 CAN_H
5 CAN_L
6 SYNC_L
7 Sync7 – reserved
8 Sync8 – reserved
NB: Using a CAT5 ethernet cable strip back the cable and connect to pins identified above.
Step 4 - Select Canbus protocol to "SmaSunnyIslandV31" and Save.
  • Limited power must be enabled.
  • When the bypass current for all cellmons is above Final the system will complete charging cycle.
Note: Make sure to "Device Sync" the changes to the CellMons.
  • Scaling must be 100 for voltage.
  • Scaling must be 10 for current.
Step 11 - Adjust the remote discharging targets to suit the application.
  • Do not run low power mode on discharging tab.
  • Control logic discharge voltage cutout should match the remote target.
Step 12 - Navigate to Telemetry, then Live Stats to observe system operation.
Step 13 - Navigate to Control, then Remote to observe inverter info received
  • Charge Target Voltage - voltage cutout sent to inverter when charging
  • Charge Target Current - ampere limit sent to inverter when charging
  • Charge Actual Flags -  reported charging mode and operating state flag received from inverter
  • Charge Actual Voltage - charging cutout volatge setpoint sent from inverter
  • Charge Actual Current - reported battery amperes from inverter when charging
  • Charge Actual Power - reported battery state of charge SoC% received from inverter
  • Charge Actual Temperature - reported battery temperature from inverter
  • Discharge Target Voltage - voltage cutout sent to inverter when discharging
  • Discharge Target Current - ampere limit sent to inverter when discharging
  • Discharge Actual Flags - reported active message error flag received from inverter
  • Discharge Actual Voltage - reported battery voltage from inverter
  • Discharge Actual Current - reported battery amperes from inverter when discharging
  • Discharge Actual Power - reported relay state flag received from inverter
  • Discharge Actual Temperature - not used
  • Live statistics telemetry