How to control a Victron Color Control GX with a WatchMon
Victron Color Control GX CCGX Monitoring panel online display for VRM and APP
Here are the steps to configure the Victron Color control GX to the WatchMon supervisor.
CAUTION:  Example below has values shown for a demo LiFePO4 cell pack, ensure that you adopt values suitable to your application and comply with the battery suppliers recommendation.
Step 1 - Install communication cable to CAN port on WatchMon.
Step 2 - Install communication cable to Victron CCGX canbus socket (extract from manual)
Plug the CCGX side of that cable into one of the VE.Can sockets on the back of the CCGX. Plug the other end into the battery. Then, plug a VE.Can terminator in the other VE.Can socket on the CCGX.
Custom Cable pinout for CCGX
Function VE.Can RJ-45 Watchmon
GND Pin 3 Supply negative / ground
CAN-L Pin 8 CAN low
CAN-H Pin 7 CAN high
For reference here’s an ethernet plug diagram. Be aware that some ethernet cables may vary.
To make up the custom ethernet cable for the CCGX properly you should use a proper crimper and fresh RJ45 male connectors. Label both ends of the cable and install it.
Step 4 - Select Canbus protocol to "Victron ColourControl GX" and Save.
  • Low power must be enabled.
  • When the bypass current for all cellmons is above Final the system will complete charging cycle.
Note: Make sure to "Device Sync" the changes to the CellMons.
  • Scaling must be 10 for both voltage and current.
Step 11 - Adjust the remote discharging targets to suit the application.
  • Do not run low power mode on discharging tab.
  • Control logic discharge voltage cutout should match the remote target.
Step 12 - Navigate to Telemetry, then Live Stats to observe system operation.
Step 13 - Within Victron software - VEConfigure settings
13.1 General tab
  1. Check “Enable battery monitor”
  2. Enter the battery capacity in Amp Hours (i.e. 120.0 Ah)
  3. The other parameters (“State of charge when bulk finished” and “Charge efficiency”) can be left to their default setting. They are not used in this setup.
13.2 Charger tab
Parameter Setting
Battery type Lithium
Charge curve Fixed
Absorption voltage 60.75 V
Float voltage 60.00 V
Absorption time 1 Hr
Note: make sure to double check the float voltage after completing Assistants, and if necessary set it back to 60.00 V.
This needs to be adjusted to match the BMS operating targets
13.3 ESS Assistant
Select the fourth battery type:
Then:
  1. Do not change the dynamic cut-off values, they have already been set correctly after selecting the lithium battery type.
  2. Sustain voltage: 50V
  3. Same for the restart offset: do not change that.
Step 14. Within Victron software - device configuration
  • Select the CAN-bus BMS (500 kbits/s) CAN-profile in the Venus device. Menu path: Settings → Services → CAN-profile. Note that this changes the function of a VE.Can port: it is not possible to connect both VE.Can products and a BMS battery together on a Color Control GX.
  • Select CAN-bus BMS (500 kbit/s)
  • After properly wiring and setting up, the BMS the ESS will be visible as a battery in the device list:
  • The parameters option within the battery page shows the actual battery charge and discharge limits:
  • Live Statistics telemetry